I have experienced several problem regarding to the compressor motor. Our client have sent the compressor motors range between 250 HP to 450 HP. We are following standard service step by step. After dissemble the motor, we have done IR test at each phase of coil to check the healthy of the coil. Then we have cleaned the coil with high pressure water to eliminate the contaminants. After that we oven baked the stator. After the stator been taken out from oven, we do again IR Test at 1000 V. We found out that the IR dropped after it cooled down. My question is what is cause of insulation drop after clean the coil? Even after we re-varnish the coil, the IR still remain very low. Please advise how to prevent the IR from drop drastically.
Thank you
I have experienced several problem regarding to the compressor motor. Our client have sent the compressor motors range between 250 HP to 450 HP. We are following standard service step by step. After dissemble the motor, we have done IR test at each phase of coil to check the healthy of the coil. Then we have cleaned the coil with high pressure water to eliminate the contaminants. After that we oven baked the stator. After the stator been taken out from oven, we do again IR Test at 1000 V. We found out that the IR dropped after it cooled down. My question is what is cause of insulation drop after clean the coil? Even after we re-varnish the coil, the IR still remain very low. Please advise how to prevent the IR from drop drastically.
Thank you