ASHRAE Classifies heat gain into (3) as follows:
A = Motor in Driven Equip in. Btu/hr Heat gain = (BHP x 2545)/Eff
B = Motor out, Driven Equip in. Btu/hr Heat Gain = BHP x 2545
C = Motor in, Driven Equip out. Btu/hr Heat Gain = ((1-EFF)/Eff)) x BHP x 2545
My situation is as follows:
I have a 500 hp motor driving a water pump within closed room, pump is moving water at 120F, pump efficiency is 70%, motor efficiency is 95.6%,
Which equation to use to calculate heat load (heat generated) by this combo. water pumped is coming and going to and from different areas of the plant, pipe enters and exists through the wall. Need to know heat generated by both to design cooler.
Utilizing equation A generates heat load of 1,331,000 BTU/HR is this correct?
When I consider motor only Equation C I get 58,600 BTU/HR
Equation A does not use any pump info, however it generates huge load as compare to equation C.
If I will treat them separately and calculate motor load using C and how do I calculated pump load?
I know that maximum pump casing can reach 180F
A = Motor in Driven Equip in. Btu/hr Heat gain = (BHP x 2545)/Eff
B = Motor out, Driven Equip in. Btu/hr Heat Gain = BHP x 2545
C = Motor in, Driven Equip out. Btu/hr Heat Gain = ((1-EFF)/Eff)) x BHP x 2545
My situation is as follows:
I have a 500 hp motor driving a water pump within closed room, pump is moving water at 120F, pump efficiency is 70%, motor efficiency is 95.6%,
Which equation to use to calculate heat load (heat generated) by this combo. water pumped is coming and going to and from different areas of the plant, pipe enters and exists through the wall. Need to know heat generated by both to design cooler.
Utilizing equation A generates heat load of 1,331,000 BTU/HR is this correct?
When I consider motor only Equation C I get 58,600 BTU/HR
Equation A does not use any pump info, however it generates huge load as compare to equation C.
If I will treat them separately and calculate motor load using C and how do I calculated pump load?
I know that maximum pump casing can reach 180F