HiLevel
Electrical
- Aug 3, 2006
- 17
I have a gas rack located a distance away from an enclosed duct burner. It's a typical gas rack with <5 psig natural gas. The design engineer has classified the area around the gas rack as Class I Group D Division 2. And, the result is a big change order and delay from the gas rack manufacturer. There are no other sources of flammable gas in the area, only the natural gas in the pipe. The design engineer is looking at codes like NFPA 497 and API 500 figure 104 to justify the classification. Their position is that the gas rack contains numerous threaded connections and devices such as SSOVs, and instruments that make it a high risk area. However, if this is the case, why don't the burner manufacturers design their systems to meet this classification? I know that NFPA and API both say you don't have to classify an area around a flame; duuuh. But, I don't have this typical condition to fall back on this time. I also know that the codes API 500 5.4.2 and others allude to lighter than air gases (natural gas) being less likely to accumulate; however, they don't go to the point of recommending classifications.
Why don't the burner and gas rack manufacturers build their systems to meet this classification if these standards are truly applicable.
Does anyone know of a reference? I also looked at AGA and they don't seem to get into electrical classification at all.
Thanks ahead of time!
Bill
If you think I'm in the wrong forum with this please let me know!
Why don't the burner and gas rack manufacturers build their systems to meet this classification if these standards are truly applicable.
Does anyone know of a reference? I also looked at AGA and they don't seem to get into electrical classification at all.
Thanks ahead of time!
Bill
If you think I'm in the wrong forum with this please let me know!