References:
1. "Getting Started Basics and Installation, PSCAD/EMTDC Version 3.0," Revision 3.0.4 - 8 June 2000
2. "Introduction to PSCAD/EMTDC V3" dated March 31, 2000, Rev. 1.3
Response to the previous posting:
1. The software is very suitable and accurate for modeling transient phenomena, which was not denied anywhere, and it is included in Reference 1 "Foreword." This is in agreement with the above postings. What is at a question are symmentrical component models suitable for the steady state load flow, short circuit and voltage drop analysis, especially a suitability to align them with any particular industry standards. There are no references cited to any industry standards in Reference 1, except perhaps over the Help System in EMTDC User's Guide.
2. Reference 2 "Table of Contents" does not really list Generators and Motors; however, it does list Transformers, Transmission Lines and Surge Arresters. It seems to be referring to academic papers and few industry standards, which is excellent for its purpose pertaining to transient models, however, less convenient for practical applications and equipment meeting industry standards. There is an enormous amount of practical and theoretical knowhow needed for proper correlations. For example, where to fit "Closing and Latching Capability" under Circuit Breakers in Reference 2 Section 7-10.
3. The generator positive, negative and zero sequence parameters and their relationships to subtransient, transient and synchronous reactances seems to be omitted from References 1 and 2.
4. The software and its results cannot easily be compared to industry widely used software, e.g. DAPPER, ETAP, etc.
5. Etc.