Rehacayli
Mechanical
- Aug 1, 2013
- 14
Dear all,
I've found similar questions but not the exact answer. I have 3 electrical rooms with only circuit breakers, UPS and panels inside. According to NFPA 13@s below statement, I don't need to put any sprinkler or protection system inside. Now my question is for the third item. Is that talking about the room or the panels; as the room itself has 2 hours protection but the panels don't have that. Another question is; I've installed CO2 extinguishing system inside the room but because it is dangerous, the owner wants to cancel that. Could anyone tell me how dangerous it is? In the light of these shall I change the protection system or shall I cancel it completely?
8.15.10 Electrical Equipment.
8.15.10.1 Unless the requirements of 8.15.10.3 are met, sprinkler
protection shall be required in electrical equipment rooms.
8.15.10.3 Sprinklers shall not be required in electrical equipment
rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure
including protection for penetrations.
(4) No combustible storage is permitted
I've found similar questions but not the exact answer. I have 3 electrical rooms with only circuit breakers, UPS and panels inside. According to NFPA 13@s below statement, I don't need to put any sprinkler or protection system inside. Now my question is for the third item. Is that talking about the room or the panels; as the room itself has 2 hours protection but the panels don't have that. Another question is; I've installed CO2 extinguishing system inside the room but because it is dangerous, the owner wants to cancel that. Could anyone tell me how dangerous it is? In the light of these shall I change the protection system or shall I cancel it completely?
8.15.10 Electrical Equipment.
8.15.10.1 Unless the requirements of 8.15.10.3 are met, sprinkler
protection shall be required in electrical equipment rooms.
8.15.10.3 Sprinklers shall not be required in electrical equipment
rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure
including protection for penetrations.
(4) No combustible storage is permitted