I have been searching for the right Fire suppression for Electrical room through NFPA , IBC , articles in internet talking about Electrical Equipments fire protection and i went through some posts here in the forum which discussed the same topic.some forum members suggest gaseous fire extinguishing system as some articles do.But that proposal of gaseous fire extinguishing system contradicts what NFPA 13 mentioned clearly as NFPA 13 mandates the use of fire sprinklers in Electrical room unless some certain conditions are met. I'm confused and not able to reconcile those 2 opposite points of view together.Plz advise as i face alot of electrical rooms in the projects I'm working on and it's always designed as Fm 200 which I find costly without need for the owner.
8.15.11 Electrical Equipment.
8.15.11.1 Unless the requirements of 8.15.11.2 are met, sprinkler protection shall be required in electrical equipment.
rooms.
Sprinklers shall not be required in electrical equipment
rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure
including protection for penetrations.
(4) No combustible storage is permitted to be stored in the
room
8.15.11 Electrical Equipment.
8.15.11.1 Unless the requirements of 8.15.11.2 are met, sprinkler protection shall be required in electrical equipment.
rooms.
Sprinklers shall not be required in electrical equipment
rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure
including protection for penetrations.
(4) No combustible storage is permitted to be stored in the
room