Suggestions/comments to the previous posting marked ///\\Mondy (Electrical) May 4, 2004
Hi everyone
My main concern was just calculating with reasonable accuracy the no load rms current of transformers/coils wound on a particular grade of steel.
///Usually, the fundamental sinusoidal waves are used since the transformer is supposed to operate in the linear region. The nonlinear region is left to transients, overloads, inrushes, etc.\\It is (or was!) common for core material suppliers to supply two curves for power use namely Watts/Kilogram and VA/Kilogram for a given frequency and a range of flux densities (say 0.1 to 2 tesla) To calculate the no-load current you just looked up the VA/kg at the corresponding working flux, multiplied it by the weight of the core and divided the rms working voltage into this figure to come up with the no-load current. Now however it seems that the Watts/kg is given as usual (and arguably the most important curve) but instead of VA/kg, they provide an AC Magnetization curve that represents Peak Magnetic Field Strength (in Amps per meter) as a function of Peak Flux density. To me this would be OK if it was RMS Magnetic Field strength as all you would need to do was to Multiply this figure by the Magnetic Path length of the core and divide this by the turns to get the RMS no-load current.
///The given magnetization curve is supposed to be used in its linear portions for the transformer operation in the linear region.\\ However as it shows only peak values, how can you determine the RMS value as towards the higher flux densities (and the nearer you get to saturation) the no-load current departs from a sinusoidal shape and gets strongly peaky. How then can you establish the rms value of the no-load current?
///The linear portion suffices. The nonlinear portion will provide additional results for the transformer operations in the nonlinear region.\\Sergio, could you give me your method of calculating the Inrush current of transformers so that you can ensure that it is at least below a certain level? I have never really seen a method to do this. I have always been shown to calculate the approximate coil inductance using 20 as the permeability of the material (?!), and then add the resulting impedance at the working frequency to the coil DC resistance (in quadrature) to come up with the lump impedance and then just dividing this by the peak voltage applied to the coil.
///Taking the worst case in some parameters is often done in the design process. By obtaining the more accurate lower values, the design is more accurate; however, the margin due to most conservative value is not there.\\ To my mind this seemed a little too rule of thumb and although the majority of "practical" transformer equations are of this sort, I thought that a better method should be sought, but so far no luck. The majority of customers of small transformers just need to know a worst-case scenario.
///Yes, this seems to be the case, namely, to get the most for their money.\\It seems that on the net and in general there is an awfull lot of theoretical information and very little practical application information regarding all spects of transformer design.
///This is just to have a good insight, which phenomena take place, how good is the worst case or more conservative value, etc.\\