trosepe
Electrical
- Mar 28, 2009
- 82
Does anyone have any experience, good or bad, with 'Electroflow Power Conditioners'. The claim is they reduce energy costs, system losses and harmoics and improve PF. They have been applied in plant that has 50% of the motor load controlled by VFD.
The plant load is 4.1MW and 1.4MVAR. There are about 1MVAR of these electroflow units connected at the main 480v swbds. They connected them in parallel with existing feeder circuit breakers to the MCC's. The plant has approx 700KVAR of static capacitors connected at the larger 480V motors.
With all the electroflow power conditioners off, the plant PF os .89 and THD is 2.2%. They have been loosing an inordinate number of drives latley; just several months after the installation of the electroflow equipment. I have advised the to leave the electroflow units disconnected until the affect is evaluated.
They seem to be just switched capacitor banks. I am concered with over correction of the plant PF and resonance with the harmonics from the drives. Anyone that has experience with these or similar units please let me know what your experiences were. Thanks.
The plant load is 4.1MW and 1.4MVAR. There are about 1MVAR of these electroflow units connected at the main 480v swbds. They connected them in parallel with existing feeder circuit breakers to the MCC's. The plant has approx 700KVAR of static capacitors connected at the larger 480V motors.
With all the electroflow power conditioners off, the plant PF os .89 and THD is 2.2%. They have been loosing an inordinate number of drives latley; just several months after the installation of the electroflow equipment. I have advised the to leave the electroflow units disconnected until the affect is evaluated.
They seem to be just switched capacitor banks. I am concered with over correction of the plant PF and resonance with the harmonics from the drives. Anyone that has experience with these or similar units please let me know what your experiences were. Thanks.