At a new installation, a rectifier is feeding a DC electrolytic cell making sodium hypochlorite (bleach). The rectifier is rated 110 KW input three phase, 480 volt 60 Hz.It has a tranformer input and its design at rated load is 90% power factor with an IEEE 6 pulse type harmoinic current distribution. The source is a 480/277 volt grounded wye system.
At about full load, the 5th harmonic current is about twice the expected value and the 7th is about 1.5 X times the design value. The power factor at about full load is 60% and it remins the same at lower loads.
To make a long story short, the indications are that the rectifer is OK and there is now suspicion that the electrolysis cell is not behaving as a typical R or XL type load and that there is some other dynamic prcoeess occurring causing these strange conditions.
Does any one have any insight into this?
Thank you JIM