psuzig
Electrical
- May 17, 2004
- 1
Hi folks. I was hoping someone could help clarify the application of an old Westinghouse CO-8 protective relay and associated CT's. The CO-8 relay in question has a tap setting range of 1 - 12, 1200:5 CT's, and is protecting a 1,200 amp feeder. It's my understanding that the tap setting is directly related to the long time pickup current rating of the device. For example, if a tap of 5 is selected, the pickup current would be ( 1200 / 5 ) x 5 = 1,200 amps. With this example in mind, I have two questions:
1. Does the pickup current rating establish the overcurrent protective device rating for the circuit/feeder?
2. When would a tap setting above 5 be used with XXXX:5 CT's? Several engineers that I work with believe that if the CT's have a secondary rating of 5, any tap setting above 5 will potentially saturate the CT's. i.e. In the example above, if a tap of 12 was selected, the pickup current would be ( 1200 / 5 ) x 12 = 2,880 amps, well above the 1,200 amp CT primary rating and 1,200 amp feeder ampacity.
Thanks for your help.
1. Does the pickup current rating establish the overcurrent protective device rating for the circuit/feeder?
2. When would a tap setting above 5 be used with XXXX:5 CT's? Several engineers that I work with believe that if the CT's have a secondary rating of 5, any tap setting above 5 will potentially saturate the CT's. i.e. In the example above, if a tap of 12 was selected, the pickup current would be ( 1200 / 5 ) x 12 = 2,880 amps, well above the 1,200 amp CT primary rating and 1,200 amp feeder ampacity.
Thanks for your help.