Elementary Question on Electrical Power 3
Aishah
1
Hi Electrical Gurus,
I have an elementary question on calculating the electrical energy consumed by an air-conditioner. That is, one of my technicians reports his measurements that goes like this: Current R/S/T = 12.9/10.3/11.6 Amps and Voltage R/S/T = 216/231/225 Volts. I know that to calculate the power (in W) is an easy thing using P = sqrt(3) * V * I * PF.
But in my case, which current and voltage do I need to plug in the P-equation? Can I use the average current and voltage in that formula?
Thank you for your answer(s)
Aishah
Yes you can use the average to get an approximate answer.
You can also take each amperage x the voltage and add the 3 up. How close do you need to be? I am not familar with the terms R/S/T. Is the the phase readings? We usually use
A,B and C to designate the phase voltage and current.
I never heard of the R/S/T thing either put my guess would be that these mean that the unit can run at either of these voltages. Is this a 3-phase unit? If you are running at 225V, use the 11.6A. If you are running at 231V, use the 10.3A. Maybe I am wrong, but without more info this is what I'd say.
R/S/T is European terminology. It probably originates at the same time as the U/V/W notation.
One day my ship will come in.
But with my luck, I'll be at the airport!
Multiply R amps x R volts = R volt amps.
Do the same for S & T phase and add the VA up to get total VA (Volt Amps) consumed. The root 3 factor does not apply since these are single phase voltages (line to neutral).
Watts = Volt amps x power factor.
You will have to take a guess on the power factor of the AC unit. It is probably about 0.85 - 0.9. If any electric heating elements are operating, they will be at 1.0 power factor and pull the total power factor higher (0.9-0.95).