- 8
All,
This may be a really stoooopid question, but I'll ask anyway...
During hydraulic calculations for sprinklers, we have to account for water flowing up the pipe (such as risers and riser nipples) by multiplying the elevation difference by 0.433. Easy enough.
But what if we are "losing" elevation? For example, if I drop 1 ft from my branchline to my sprinkler head (arm over) do I ignore the 1 ft drop or do I now have "negative" pressure since the water is flowing down vs. up?
Up to this point I have been ignoring the "negative" pressure and just making sure I accounted for water rising up pipe.
How have you guys worked it? Am I doing it right or am I in trouble?
Thanks in advance.
Shawn Lee, CET
Fire Alarm Systems Level III
Sprinkler Newbie