eliminate a PILZ

Status
Not open for further replies.

gilgora

Industrial
May 22, 2008
4
hi everyone someone can explain me the diference between protective relay (like PILZ) and a latching relay or solid relay what I know is than protect against overcurrent and responde with a timer or somthing like that, because I have and old PILZ with 2 normally open contacts and Y1 and Y2 to reset the PILZ but in Y1 and Y2 there is a bridge so I dont think I need another PILZ maybe just a latching relay with a fuse or something like that, this PILZ enable 24vdc for the outputs of a PLC and cut off when press the emergency stop, what do you recommend to change it?
 
Replies continue below

Recommended for you

If it's bad, I'd recommend that you replace it with the same thing.

It's a special protective relay module that has 2 relays in series for the E-Stop, it checks the operation of both relays. It also contains circuitry that checks the E-Stop button circuit. If it finds a fault in any of these areas, it will go into fault and inhibit operation until the fault is cleared.

It really can't be replaced by anything other then another E-Stop module, unless you want to compromise the safety of your machine.

Ed


 