Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Emergency Stop Switch

Status
Not open for further replies.

ROCHESTER

Mechanical
Nov 2, 2002
33
0
0
US
Mech. Eng. here... Being asked to install a guard on E-Stop switch. Are there professional and/or regulatory guidelines for the design of E-stops?

Thanks,

Craig
 
Replies continue below

Recommended for you

NFPA 79 specifically addresses e-stops. Use this as your guide. E-stops must be accessible and NOT covered or recessed. OSHA does not directly spell this out, however, under their Articles of Incorporation they can use the NFPA 79 Standard on E-Stops to cite companies.

If you do not have NFPA79, a very good discussion on E-Stops is available from Square-D.

Please go to the following Square-D link to open and review pertinent standards/requirements presented in Appendix C pages 319-322 of their Safety Catalog:

David Baird

Sr Controls Designer
EET degree.