I would like peoples opinion on the term 'encapsulated' anchorage who are familiar with PTI's specifications, unbonded Post Tensioning slabs & also construction in 'agressive' areas such as coastal construction & parking garages.. This is specifically as regards construction in East Central Florida on the ocean/barrier islands..
Here is a link to PTI's page with an 'encapsulated' anchorage.. They may change this link, but I will try to describe it.
At the end anchorage the commonly used & locally supplied systems have an (epoxy or similar) coated area that has an 'end cap' (filled with grease). On the inside of the end anchorage there is a transition tube ~12/16" long that has a locking ring that connects the 'sleeve' (also referred to as a trumpet') to the anchor.. There is also a washer that the sheathing goes into as it enters the tube. According to PTI there should be 4" minimum embedment of the sheathing into the sleeve'.. The system is also supposed to be watertight to 3 foot head of water (~200 psf)..
PTI uses the words 'no voids'in their description of an 'encapsulated' system.. The way that I interpret that is that the 'sleeve' should be filled with grease (as indicated on the picture on their website).. This seems very logical when one considers that this system is to be used in an ‘aggressive’ environment and that the ends are an easy entry point for water borne chlorides and thus corrosion. In my opinion the ‘sleeve’ and whole end anchorage area should be at least as watertight and moisture resistant as the main sheathing. Rust requires the presence of air & water, & chlorides accelerate this process. I would like some independant interpretions of 'no voids'.. I have ordered the PTI spec on unbonded tendons, but do not have it on hand and will quote the full text when it arrives.. If anyone out there has access to it, please quote for me..
I am EOR and Threshold Engineer for a 4 story building beachside. What appeared on my jobsite, however, was not what was in the picture posted on PTI’s website as an ‘encapsulated’ anchorage.. The 'sleeve' was not 'filled' with grease & I could not see if the cable was completely coated with grease, and the void was actually 'filled' with (moist) air and there was visible condensation on the insides of the sleeve'. Additionally the 'locking rings were not in place and in a few locations the sleeve was not connected to the anchorage. The end caps were not translucent, but upon removal & inspection were filled with grease..
In addition, apparently during laying out of the cables, the sheathing was pulled away from the anchorage & sleeve and as much as 6" was fully exposed.. PS 'duct tape' wrap is not a legit fix - especially in anchorage areas. Water will leak..
The PT supplier said that I should have specified a 'fully encapsulated' system if I wanted the voids filled with grease.. PTI's technical Director said that there is also a 'propitiatory' system (not my supplier) that is 'fully encapsulated', but is it not of one of PTI's standard systems ('regular' & 'encapsulated') .. PTI's field/certification rep (?) and apparently the local Florida suppliers (or is it just our own) interprets that as not having a void in the grease surrounding the cable in the sleeve.. I beg to differ and would like other design engineers interpretations..
Thank god the contractor I am working for/with is going ahead & getting grease delivered to add in the field & fill the 'sleeves'. Hopefully it will not be a real mess, but I am sure there will be a lot of moaning & groaning by the workers.
I wonder if many of you have encountered the same condition that I have here.. One of the many disturbing things is that there may be a lot of buildings out there that have 'sleeves' that are not filled with grease but the EOR's think that they are.. I also thought that the PT industry was more regulated that it actually is.. Is this just in Florida or nationwide?
One of the lecturers at a seminar a few years ago said that PT anchorage problems were going to replace the asbestos fiasco of the 80’s & 90’s.. I now see what he meant..
Here is a link to PTI's page with an 'encapsulated' anchorage.. They may change this link, but I will try to describe it.
At the end anchorage the commonly used & locally supplied systems have an (epoxy or similar) coated area that has an 'end cap' (filled with grease). On the inside of the end anchorage there is a transition tube ~12/16" long that has a locking ring that connects the 'sleeve' (also referred to as a trumpet') to the anchor.. There is also a washer that the sheathing goes into as it enters the tube. According to PTI there should be 4" minimum embedment of the sheathing into the sleeve'.. The system is also supposed to be watertight to 3 foot head of water (~200 psf)..
PTI uses the words 'no voids'in their description of an 'encapsulated' system.. The way that I interpret that is that the 'sleeve' should be filled with grease (as indicated on the picture on their website).. This seems very logical when one considers that this system is to be used in an ‘aggressive’ environment and that the ends are an easy entry point for water borne chlorides and thus corrosion. In my opinion the ‘sleeve’ and whole end anchorage area should be at least as watertight and moisture resistant as the main sheathing. Rust requires the presence of air & water, & chlorides accelerate this process. I would like some independant interpretions of 'no voids'.. I have ordered the PTI spec on unbonded tendons, but do not have it on hand and will quote the full text when it arrives.. If anyone out there has access to it, please quote for me..
I am EOR and Threshold Engineer for a 4 story building beachside. What appeared on my jobsite, however, was not what was in the picture posted on PTI’s website as an ‘encapsulated’ anchorage.. The 'sleeve' was not 'filled' with grease & I could not see if the cable was completely coated with grease, and the void was actually 'filled' with (moist) air and there was visible condensation on the insides of the sleeve'. Additionally the 'locking rings were not in place and in a few locations the sleeve was not connected to the anchorage. The end caps were not translucent, but upon removal & inspection were filled with grease..
In addition, apparently during laying out of the cables, the sheathing was pulled away from the anchorage & sleeve and as much as 6" was fully exposed.. PS 'duct tape' wrap is not a legit fix - especially in anchorage areas. Water will leak..
The PT supplier said that I should have specified a 'fully encapsulated' system if I wanted the voids filled with grease.. PTI's technical Director said that there is also a 'propitiatory' system (not my supplier) that is 'fully encapsulated', but is it not of one of PTI's standard systems ('regular' & 'encapsulated') .. PTI's field/certification rep (?) and apparently the local Florida suppliers (or is it just our own) interprets that as not having a void in the grease surrounding the cable in the sleeve.. I beg to differ and would like other design engineers interpretations..
Thank god the contractor I am working for/with is going ahead & getting grease delivered to add in the field & fill the 'sleeves'. Hopefully it will not be a real mess, but I am sure there will be a lot of moaning & groaning by the workers.
I wonder if many of you have encountered the same condition that I have here.. One of the many disturbing things is that there may be a lot of buildings out there that have 'sleeves' that are not filled with grease but the EOR's think that they are.. I also thought that the PT industry was more regulated that it actually is.. Is this just in Florida or nationwide?
One of the lecturers at a seminar a few years ago said that PT anchorage problems were going to replace the asbestos fiasco of the 80’s & 90’s.. I now see what he meant..