Buildtech2
Mechanical
- Mar 6, 2012
- 158
The total area of enclosed carpark is 47817 sq.ft. As per client requirement, the ventilation to this car park shall be based on NFPA 88A standard which is 1 cfm per sq.ft. Therefore the total ventilation air required would be 47817 cfm.
Since the total area of my basement car park is 47817 sq.ft. and CO sensor location requirement is every 5000 q.ft. I am unable to take a decision whether I should go for ducted intake and exhaust system or wall mounted intake and exhaust system with several jet fans which will be interlocked with CO sensors.
As an option, we can propose a main exhaust intake fan and supply fan (both with VFD) with capacity of 47817 cfm and in addition to this, there will be several jet fans which will be interlocked with co sensors. I have selected 18 jet fans of maximum air flow of 2669 cfm and minimum air flow of 1356 cfm.
Questions:
1. Is it required to run the main exhaust and supply fans continuously at low speed under normal operation even if there is no requirement of any jet fan to be operated based on CO sensor..
2. Do we need to consult a supplier for CFD analysis and calculation for car park ventilation.
3. Imagine if only 4 jet fans runs at a particular time at low speed, the air flow of these fan will not be equal to the main exhaust fan and supply fan even at low speed. How can we balance it.