richburton
Specifier/Regulator
- Dec 11, 2009
- 19
It should seem reasonable that a stand-alone commercial garage with five or six parking bays will not have a sprinkler system. It should seem reasonable that it will not have a mechanical ventilation system.
IBC 903.2.10 would exempt any enclosed parking garage from being sprinkled if the fire area is less than 12,000 S.F. And we are not talking about a repair garage or the storage of commercial vehicles weighing more than 10,000 lbs each.
In other words, such a garage could be a basic plywood box without power, water, or heat. Add six overhead garage doors measuring 8 feet wide and we are done. Right?
Meanwhile, we take a look at NFPA 88A Standard for Parking Structures. Below is the relevant excerpt:
6.4.3 Automatic sprinkler systems shall be installed in enclosed parking structures located at or above grade, or within or immediately below a building used for another occupancy.
Exception: Enclosed parking structures described above, having an approved, supervised, automatic fire detection system and alarm system installed throughout the parking area in accordance with NFPA 72 and a mechanical ventilation system in accordance with 5.3.2.
6.6.2 An approved, supervised, automatic fire detection and alarm system shall be installed in enclosed parking structures having a mechanical ventilation system, located at or above grade, or within or immediately below a building used for another occupancy.
Exception: Enclosed parking structures described above in 6.6.2, having an approved automatic sprinkler system installed throughout in accordance with NFPA 13.
3.3.2.3 Parking Structures, Enclosed. Any parking structure that is not an open parking structure.
- - - end of NFPA 88 excerpts
Question:
I do not believe that a simple commercial garage needs a sprinkler system. I do not believe that it needs an alarm system. I do not believe that it needs a mechanical ventilation system. What exceptions (within the NFPA codes) are there for not requiring either a sprinkler system or an alarm system?
Thank you,
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
IBC 903.2.10 would exempt any enclosed parking garage from being sprinkled if the fire area is less than 12,000 S.F. And we are not talking about a repair garage or the storage of commercial vehicles weighing more than 10,000 lbs each.
In other words, such a garage could be a basic plywood box without power, water, or heat. Add six overhead garage doors measuring 8 feet wide and we are done. Right?
Meanwhile, we take a look at NFPA 88A Standard for Parking Structures. Below is the relevant excerpt:
6.4.3 Automatic sprinkler systems shall be installed in enclosed parking structures located at or above grade, or within or immediately below a building used for another occupancy.
Exception: Enclosed parking structures described above, having an approved, supervised, automatic fire detection system and alarm system installed throughout the parking area in accordance with NFPA 72 and a mechanical ventilation system in accordance with 5.3.2.
6.6.2 An approved, supervised, automatic fire detection and alarm system shall be installed in enclosed parking structures having a mechanical ventilation system, located at or above grade, or within or immediately below a building used for another occupancy.
Exception: Enclosed parking structures described above in 6.6.2, having an approved automatic sprinkler system installed throughout in accordance with NFPA 13.
3.3.2.3 Parking Structures, Enclosed. Any parking structure that is not an open parking structure.
- - - end of NFPA 88 excerpts
Question:
I do not believe that a simple commercial garage needs a sprinkler system. I do not believe that it needs an alarm system. I do not believe that it needs a mechanical ventilation system. What exceptions (within the NFPA codes) are there for not requiring either a sprinkler system or an alarm system?
Thank you,
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner