anythingwithawire
Electrical
- Nov 27, 2009
- 4
Hi
I do a bit of troubleshooting work in the marine industry and seem to be coming up against one particular problem over and over - electronic diesel engine controllers by Wartsila (WECS series) on medium/large (say 500kW to 2MW) reciprocating diesel engines for generators.
There are edge coneector cards, small potentiometers and relays in these things and apart from premature failure, there seems to be problems with resonance on the relay armatures causing false shutdowns under certain semi-repeatable conditions.
You can see the whole unit vibrating at different frequencies at different times and the are all sort of mechanical beat frequencies and harmonics going on. I have seen many, many part or complete failures in equipment less than 3-5 years old, the current one only 9 months and 2 out of 5 are tripping intermittantly with no indication.
Wartsila have advised to remove some connectors/plugs for one of the units, but now the 1.5MW diesel is unprotected for some functions. (but it is running without tripping, fantastic - sarcasm always works for me). Meanwhile they are sending someone out from the factory in '2 or 3 weeks'. Cost of blackout on this deal is up to maybe 70 million if not recovered quickly enough due to equipment damage and contractual issues. (I am trying to be a little general here for commercial reasons).
The mounting of these systems on the engine just seems flat out dumb and I can't see why you would do such a stupid thing when the engine room environment is already very harsh, and then they pick the worst possible place to put them.
Has anyone got any comments. I can post a photo later, but I am on a boat right now with limited bandwidth.
Thanks
AnythingWithAWire.
I do a bit of troubleshooting work in the marine industry and seem to be coming up against one particular problem over and over - electronic diesel engine controllers by Wartsila (WECS series) on medium/large (say 500kW to 2MW) reciprocating diesel engines for generators.
There are edge coneector cards, small potentiometers and relays in these things and apart from premature failure, there seems to be problems with resonance on the relay armatures causing false shutdowns under certain semi-repeatable conditions.
You can see the whole unit vibrating at different frequencies at different times and the are all sort of mechanical beat frequencies and harmonics going on. I have seen many, many part or complete failures in equipment less than 3-5 years old, the current one only 9 months and 2 out of 5 are tripping intermittantly with no indication.
Wartsila have advised to remove some connectors/plugs for one of the units, but now the 1.5MW diesel is unprotected for some functions. (but it is running without tripping, fantastic - sarcasm always works for me). Meanwhile they are sending someone out from the factory in '2 or 3 weeks'. Cost of blackout on this deal is up to maybe 70 million if not recovered quickly enough due to equipment damage and contractual issues. (I am trying to be a little general here for commercial reasons).
The mounting of these systems on the engine just seems flat out dumb and I can't see why you would do such a stupid thing when the engine room environment is already very harsh, and then they pick the worst possible place to put them.
Has anyone got any comments. I can post a photo later, but I am on a boat right now with limited bandwidth.
Thanks
AnythingWithAWire.