Thank you Brad805 for this information. A structural engineer (me) is investigating because this is a place of worship and I am a member there and was asked what should be done now. The actions and principles are similar to the effects that structural engineers deal with daily, whether they are designing wood or concrete and must consider the effects of shrinkage and expansion, so it is not totally illogical to have a structural engineer involved. Of course it would likely be better to have someone who has a lot of experience with laminated flooring but we don't have such. The information that you have provided is interesting. Thank you again.
Are you aware of buckling having been caused by the air conditioing? The buckliong occurred on a weekend when the room was full of people and the air conditioning was on that week. The air conditioing (and the people) increases the RH because cold air can hold less moisture than warm air. This is what mechanocal engineers tell me is the case unless slecial demudifying provisions are built into the system, which is not the case in our building. Others to whom I have spoken attibute the most likely casue to the air conditioing and the lack if any expansion space at the end of the flooring boards where they met the wall.
The manufacturer's printed instructions seem to me almost impossible to meet, in that they require the RH in the room to be betwen 45% and 55% when installing the flooring...can be done, but would require special controls on the environment. And there are other stringent requirements that are required to be met when installing.
If this had been my project, I would have retained an inspection and tsting company to carry out site review during installation to verify, at least on a random sampling basis, that the work was being carried out in general accordance with the manufacturer's specifications. I alos reoutinely speciy that the manufacturer's representative visit the site at least once at the start of the work, to verify that the cntractor understands what is to be done to neet the manufacturer's specification.