MechProjectEng
Mechanical
- Jul 6, 2012
- 31
Hello all,
Hoping for some advice:
I work on a large industrial site, and a few weeks ago, we had a site wide power failure caused by a short circuit of one of our 11kV switchboards due to flooding.
The site is served by 2 incoming 11kV feeders, and then distributed by 6 seperate 11kV rings (Ring 1 to 6).
The fault occured on one of these rings (Ring 2). However, the fault caused the main incoming 11kV breaker to trip, causing all rings to de-energize.
Following the incident and subsequent re-energization of the facility, the following equipment damage was observed:
1. 30 No. 1000W Metal Halide Light fittings in one of our buildings burnt out (burnt out items are the capacitors, ignitors, bulbs, and 6" of the cable connected to the light fittings)
2. The power board of a 4kVA UPS burnt out.
We cannot see any technical reason for the damage other than a voltage transient/spike.
However, what is perculiar is that the damaged equipment above was connected to substations on Ring 6 (not Ring 2 where the fault occured), and there is no trace of any damage occuring closer to the source of the fault.
We are investigating the cause of the equipment damage as well as recommendations to avoid recurrance of this incident.
Your comments would be appreciated.
Thank you.
Here are some links to some photographs of the damage:
Hoping for some advice:
I work on a large industrial site, and a few weeks ago, we had a site wide power failure caused by a short circuit of one of our 11kV switchboards due to flooding.
The site is served by 2 incoming 11kV feeders, and then distributed by 6 seperate 11kV rings (Ring 1 to 6).
The fault occured on one of these rings (Ring 2). However, the fault caused the main incoming 11kV breaker to trip, causing all rings to de-energize.
Following the incident and subsequent re-energization of the facility, the following equipment damage was observed:
1. 30 No. 1000W Metal Halide Light fittings in one of our buildings burnt out (burnt out items are the capacitors, ignitors, bulbs, and 6" of the cable connected to the light fittings)
2. The power board of a 4kVA UPS burnt out.
We cannot see any technical reason for the damage other than a voltage transient/spike.
However, what is perculiar is that the damaged equipment above was connected to substations on Ring 6 (not Ring 2 where the fault occured), and there is no trace of any damage occuring closer to the source of the fault.
We are investigating the cause of the equipment damage as well as recommendations to avoid recurrance of this incident.
Your comments would be appreciated.
Thank you.
Here are some links to some photographs of the damage: