Binwork
Electrical
- Mar 4, 2024
- 2
For low voltage system 480/277V 3Phase 4 wire system.
When utility short circuit X/R is higher than equipment test X/R.
Then Equipment will face derating.
I am in NYC, I have see many buildings have 200kA 480/277 3Phase incoming short circuit with high X/R, then service equipment with 200kAic withstand raiding/ interrupt rating are not good due to derating. And I have not see any equipment are large than 200kAic.
So how do you handle this scenario? is there a solution to fix the code violation?
If there is not a solution. then how do you explain this scenario to your customer since it is violation.
When utility short circuit X/R is higher than equipment test X/R.
Then Equipment will face derating.
I am in NYC, I have see many buildings have 200kA 480/277 3Phase incoming short circuit with high X/R, then service equipment with 200kAic withstand raiding/ interrupt rating are not good due to derating. And I have not see any equipment are large than 200kAic.
So how do you handle this scenario? is there a solution to fix the code violation?
If there is not a solution. then how do you explain this scenario to your customer since it is violation.