Of course I am not allowed to perform my own test on city hydrants so they have their experts do it for me.
I like doing my own flow test because I know how to do them and my gauges are calibrated with the paperwork to go with them. I have also gotten into the habit of having someone from the fire department with me and using my phone I video tape. I don't care how pretty my drawings are if the flow test is wrong I got a pile of garbage.
ESFR system with 1,250 gpm @ 90 psi fire booster pump.
City report has 70 static, 40 residual @ 1,500 gpm (two outlets) with 1,976 gpm @ 20 psi. Sounded like we were good to go there. Nice looking report form on city letterhead and attached map showing hydrants tested. The test hydrant wasn't 100' from my fire pump.
Acceptance test yesterday and we barely made 100% @ 20 psi while running negative at 1,400 gpm. System will perform (barely) as designed as long as the 250 gpm hose stream isn't added.
Fire officials looked like a herd of deer in the headlights... test was accepted (we did get 100%) and the owner received his Certificate of Occupancy but what the heck happens if the owner wants to expand? And then the issue of the owner not getting what he paid for but I don't think I can be held accountable there.
I don't like this.
I know this has happened to everyone who has been in the game for years but just curious how others would have handled it?
I like doing my own flow test because I know how to do them and my gauges are calibrated with the paperwork to go with them. I have also gotten into the habit of having someone from the fire department with me and using my phone I video tape. I don't care how pretty my drawings are if the flow test is wrong I got a pile of garbage.
ESFR system with 1,250 gpm @ 90 psi fire booster pump.
City report has 70 static, 40 residual @ 1,500 gpm (two outlets) with 1,976 gpm @ 20 psi. Sounded like we were good to go there. Nice looking report form on city letterhead and attached map showing hydrants tested. The test hydrant wasn't 100' from my fire pump.
Acceptance test yesterday and we barely made 100% @ 20 psi while running negative at 1,400 gpm. System will perform (barely) as designed as long as the 250 gpm hose stream isn't added.
Fire officials looked like a herd of deer in the headlights... test was accepted (we did get 100%) and the owner received his Certificate of Occupancy but what the heck happens if the owner wants to expand? And then the issue of the owner not getting what he paid for but I don't think I can be held accountable there.
I don't like this.
I know this has happened to everyone who has been in the game for years but just curious how others would have handled it?