Hi,
I'm working on a small commercial building with a 1 vehicle garage. We had planned on running the exhaust of the parking garage through our ERV, which is a polypropylene plate core (2 air streams do not meet). I got into a debate with the senior engineer on the interpretation of 62.1-2007. He reads that as long as 10% or less of the volume through the ERV is from the garage it can then be used, satisfying 5.17.2.2. I argued that, that clause doesn't apply as the air streams do not mix. He disagreed because the exchanger could fail. I'm wondering if I'm interpreting the clause correctly?
I'm working on a small commercial building with a 1 vehicle garage. We had planned on running the exhaust of the parking garage through our ERV, which is a polypropylene plate core (2 air streams do not meet). I got into a debate with the senior engineer on the interpretation of 62.1-2007. He reads that as long as 10% or less of the volume through the ERV is from the garage it can then be used, satisfying 5.17.2.2. I argued that, that clause doesn't apply as the air streams do not mix. He disagreed because the exchanger could fail. I'm wondering if I'm interpreting the clause correctly?