Here are some interesting facts about that 60 second closing. Have you ever seen a 8" ballvalve open up to atmos with 900 psig behind it? Every year they would test their system and clock the blowdown.
At one site, they did the test. It only cost them about $50,000. The next year, the cost was even more. Here is what happened. All the lube oil from the compressors was laying in the headers. When they blew the gas down, all that lube oil sprayed the landowners property, cost to cleanup, $50,000. The next year they did the same thing. This time the landowner was going to sue and cancle the surface lease. I was called in and we installed 1" RO under all the 8" ball valves and piped them to a KO drum and a large single vent.
The next year it took closer to 15 minutes, but there was no oil slick.
A couple of years later I was at a different station on the day they were doing the same test. My personal car was covered with oil and the hyway outside the fence was so slick, I spun out. They had to have the road shutdown until they steam cleaned it. Needless to say, in went the RO's.