Hi Eng tips, first post for me. looks like a nice community!
I'm working on a tenant fit-out of a newly finished mixed use warehouse/office building.
The warehouse has K25.2 ESFR heads already installed in it. The heads spacing initially looked fine to me but today while on-site I noticed that there is 41"x41" concrete beams that are causing the sprinklers to not be compliant with 8.12.5.1.1.
The deflectors are 14" below the slab, this leaves 23" to the underside of the beam. Using table 8.12.5.1.1 the heads should be 5'-6" from the obstruction. However, if I space them at 5'-6" the total distance between the 2 heads on each side of the beam would be 14'-5" which is more than allowable spacing.
Is it possible to put sprinklers below the beam and treat is as a "continuous obstruction below sprinklers".
Reviewing NFPA it looks like the existing installation is not compliant and cannot be brought into compliance. If this is the case I need to notify my client.
I'm also have more senior designer in my firm review but I thought I'd try here as well.
I'm working on a tenant fit-out of a newly finished mixed use warehouse/office building.
The warehouse has K25.2 ESFR heads already installed in it. The heads spacing initially looked fine to me but today while on-site I noticed that there is 41"x41" concrete beams that are causing the sprinklers to not be compliant with 8.12.5.1.1.
The deflectors are 14" below the slab, this leaves 23" to the underside of the beam. Using table 8.12.5.1.1 the heads should be 5'-6" from the obstruction. However, if I space them at 5'-6" the total distance between the 2 heads on each side of the beam would be 14'-5" which is more than allowable spacing.
Is it possible to put sprinklers below the beam and treat is as a "continuous obstruction below sprinklers".
Reviewing NFPA it looks like the existing installation is not compliant and cannot be brought into compliance. If this is the case I need to notify my client.
I'm also have more senior designer in my firm review but I thought I'd try here as well.