Jondoeiowa
Mechanical
- Oct 6, 2011
- 29
A question has been posed at an existing manufacturing building, half the building is being converted into storage under an ESFR system. Both systems are divided by a full height wall except at a 49'-10" section. As per NFPA 13 2010 8.4.6.4.1 "Where ESFR sprinkler systems are installed adjacent to sprinkler systems with standard response sprinklers a draft curtain of noncombustible construction and at least 2' in depth shall be required to separate the two areas." This clearly calls out standard response sprinklers, would it be allowable to replace the sprinklers adjacent with Quick Response sprinklers in lieu of a draft curtain? The current division is a tapered steel beam with 6" joist chair at top.
Thank you,
Jon
Thank you,
Jon