Dear All,
Am a Mechanical Engineer dealing with Installation of HVAC system in Buildings. Have came across below issue while dealing with one of my project.
Have few Fans Located on roof of a 10 floor building which is Extracting Air from Below floor (first floor). I given the ESP calculation to a third party and the ESP calculated came very high compared to the designed ESP.
The reason is that he added a factor Pxgxh (P=Density of Air, 1.225 kg/m3., g=Gravity, 9.8 m/s2., h=Riser length of duct in meter (m) - 60 Meters). His statement was that since the flow is agaist the Gravity , this factor needs to be considered. ( Here in this case, the factor itself came = 721 pa ie: 1.225x9.81x60)
Please advise the correct method of doing the static pressure calculation for a Fan located in roof extracting air from below floor.
Note: Am capable of calculating the static pressure loss in the ducting and fittings due to friction.
Am a Mechanical Engineer dealing with Installation of HVAC system in Buildings. Have came across below issue while dealing with one of my project.
Have few Fans Located on roof of a 10 floor building which is Extracting Air from Below floor (first floor). I given the ESP calculation to a third party and the ESP calculated came very high compared to the designed ESP.
The reason is that he added a factor Pxgxh (P=Density of Air, 1.225 kg/m3., g=Gravity, 9.8 m/s2., h=Riser length of duct in meter (m) - 60 Meters). His statement was that since the flow is agaist the Gravity , this factor needs to be considered. ( Here in this case, the factor itself came = 721 pa ie: 1.225x9.81x60)
Please advise the correct method of doing the static pressure calculation for a Fan located in roof extracting air from below floor.
Note: Am capable of calculating the static pressure loss in the ducting and fittings due to friction.