Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Estimation Electrical Load

Status
Not open for further replies.

cfteh

Electrical
Oct 10, 2003
1
0
0
SG
Hi everyone,

Does anyone have any rule of thumb format in computing the estimated electrical load required for a new comerical building.

Thank.
 
Replies continue below

Recommended for you

I go 75W per square meter.

Refer to NEC 2005 Article 220 for a complete guide.

Use Australian Standard AS3000 Annex C.

Howver, The sixteenth edition of the IEE's Guide to BS7671 states in paragraph 311 that the maximum demand shall be assessed. If you have more info on this please tell me.
 
It depends on if the building uses electric heat. Typical demands I have seen for commerical office buildings are (not suitable for design purposes)-
Electric heat - 15 W/sq foot
No electric heat - 10-12 W/sq foot
 
Status
Not open for further replies.
Back
Top