ETABS P-DELTA Setup Confusion
qwop
5
I'm fairly new to ETABS and P-Delta effects and I want to make sure I have things set up correctly. I have a building that's controlled by seismic loads and I want to make sure I'm capturing P-Delta effects. My controlling load cases are below
1.2D+1.0L+1.0Ex
1.2D+1.0L-1.0Ex
1.2D+1.0L+1.0Ey
1.2D+1.0L-1.0Ey
I watched the CSI tutorial for setting up P-Delta in SAP and in that video it says to set up a static non-linear load case for each load combination you want to consider P-Delta for. So if I were in SAP my understanding is that I create 4 new static non-linear load cases, apply the same load patterns and scale factors as above, and select "P-Delta" in the geometric non-linearity option.
Now my confusion with ETABS comes in with the Define > P-Delta Options menu. Since my controlling cases use 1.2D+1.0L can I simply select "Iterative - Based on Loads" and input Dead and Live loads with the corresponding load factors and run my model without creating 4 new nonlinear load cases? Or so I still need to create those 4 cases like in the SAP tutorial video? Will my seismic load cases need to be set to non-linear if I use the P-Delta menu? Will I need to select "P-Delta" for the geometric nonlinearity option in the seismic load cases, or is that not necessary once the Define > P-Delta Options menu is used?
If it's a small building, like 8 stories or less, and it has no weird conditions like a cantilever, you can select "Iterative - Based on loads". The P-delta doesn't really matter and ETABS will make a good approximation. If it's a taller building, it becomes more complicated and I'm sure someone else will chime in.
Yes, that's my understanding. Keep in mind that this will base the P-Delta analysis on a single set of gravity loads. What you're essentially doing is a single Geometric Stiffness adjustment to the stiffness matrix based on this one set of loads. The benefit being that this then becomes a linear analysis for all load combinations. That's generally viewed as being accurate enough most of the time.
However, if you want to be a little more accurate then you could create the 4 non-linear static load cases instead. Heck, if it were me, I'd be interested in how different the results would be between the two methods.
Thank you for both of your replies. Fortunately the building is very regular and under 6 stories, so it sounds like I can use the Iterative based on loads and get a close approximation. I created a model with 4 non-linear static cases which takes a long time to run right now compared to using the P-Delta menu, but I'll compare and see what's different
Would like to know the difference you got in your models?(I believe you have already done the comparison)