When attempting to validate IEC 60909 L-G fault calculations from ETAP, I find that the fault levels are higher than I calculated. It appears that ETAP is doing
Sqrt(3) c U / |2*Z1 + Z0|,
with Z0 taken directly from the R0 and X0 in the cable library entry, rather than using Z0 = Z0 phase cable + 3*Z0 neutral cable. Is this how ETAP calculates the zero sequence impedance? This made me unsure whether the zero sequence impedance information included in the cable datasheet I have includes the neutral conductor or not. Any help is appreciated.
Sqrt(3) c U / |2*Z1 + Z0|,
with Z0 taken directly from the R0 and X0 in the cable library entry, rather than using Z0 = Z0 phase cable + 3*Z0 neutral cable. Is this how ETAP calculates the zero sequence impedance? This made me unsure whether the zero sequence impedance information included in the cable datasheet I have includes the neutral conductor or not. Any help is appreciated.