Eternal Mystery of the Universe #1 - 1-1/4" Guardrail 1

Status
Not open for further replies.

Guastavino

Structural
Jan 29, 2014
381
This issue comes up all the time for me and how it came about is one of the eternal mysteries of the universe in my mind. I always tell folks they can't use 1-1/4" STD pipe guardrail because of the 200# concentrated force at 42" makes it such that it just doesn't work in bending. Then, I get the "well it's the way we've always done it". Code officials never seem to catch it, but it doesn't work unless you start to count on a FE model that spreads the load between posts, etc. And then it's still questionable at best IMO.

Then, I see arch's spec 1.50" O.D. handrail/guardrail, which of course doesn't exist in the Pipe shape realm. So I'm curious, A) how people justify using 1-1/4" (1.66 O.D.) std pipe guardrail, and B) what do you all tell clients if you're on the same side as me, that it has to be 1-1/2" STD Pipe (1.90" o.d.)

Thanks!
 
Replies continue below

Recommended for you

If you're looking for a prescriptive design standard, then try the PIP STF05520 - "Details for Pipe Railing for Walking and Working Surfaces". The Process Industries Practice folks have a wealth of pre-configured, prescriptive, structural and civil design standards, which are used across many industries.
Dave

Thaidavid
 
since the H/R post most often is the weak link, I have used 2x2" tube for the posts, 1 1/2" std pipe for top rail and 1 1/4" std pipe for mid-rail...it also simplifies the fit-up/coping @ the mid-rail to post connection and results in more fleixibility in spacing the posts....
 