What allows IEC governed installations a much larger voltage variation limit?
IEC 60038 allows +/- 10% voltage variation under normal conditions. EN 50160 further defines normal as 95% of the time and does not have a limit for the other 5%.
ANSI C84.1 limits supply voltage to +/-5% under normal condition. Under abnormal conditions, C84.1 allows up to +6/-8% voltage variation.
The IEC 60038 allowed building voltage drop is slightly at 4% vs 5% for ANSI.
Including the building voltage drop, IEC 60038 allows +10/-14% variation. Does European equipment have a larger input range than the +/-10% suggested by the [link
] ITI (CBEMA) curve [/url]?
Thanks,
Mark Pigman
Tacoma, WA, USA