kipfoot
Structural
- Oct 25, 2007
- 492
This is more of a theoretical - judgment type question. I'm looking for a gut check, I think.
I'm working on a renovation of a 1910 (+/-) library building with a poured-in-place concrete slab supported by a steel WF girder. A couple of cuts have been made in the slab for mechanical penetrations and that has given me the chance to measure the reinforcing.
Based on what I saw (diamond mesh at the bottom of the slab supplemented with 1/2" bars) I asked that the steel be tested because it doesn't quite meet current 'library reading room' LL with my assumed fy.
For good measure, we also tested a couple concrete cores. These came back at f'c = 700 psi (I did not forget a zero). The slab exhibits top-side cracking over the girders and significant (L/200) deformation which I presume to be long term creep. This, of course, is well below current code minimum. It was an acceptable working stress at the time.
With 2000 psi concrete, the calculated capacity was close, depending on the steel strength. When I know the results of the steel test, I think I'll find that it doesn't work on paper...but it may be within 10%-20%.
So, the question is: when do you leave well enough alone if a structure has performed for 100+ years as a library and when do you say, "this slab never worked on paper and needs to be reinforced."
I'm working on a renovation of a 1910 (+/-) library building with a poured-in-place concrete slab supported by a steel WF girder. A couple of cuts have been made in the slab for mechanical penetrations and that has given me the chance to measure the reinforcing.
Based on what I saw (diamond mesh at the bottom of the slab supplemented with 1/2" bars) I asked that the steel be tested because it doesn't quite meet current 'library reading room' LL with my assumed fy.
For good measure, we also tested a couple concrete cores. These came back at f'c = 700 psi (I did not forget a zero). The slab exhibits top-side cracking over the girders and significant (L/200) deformation which I presume to be long term creep. This, of course, is well below current code minimum. It was an acceptable working stress at the time.
With 2000 psi concrete, the calculated capacity was close, depending on the steel strength. When I know the results of the steel test, I think I'll find that it doesn't work on paper...but it may be within 10%-20%.
So, the question is: when do you leave well enough alone if a structure has performed for 100+ years as a library and when do you say, "this slab never worked on paper and needs to be reinforced."