- Oct 21, 2002
- 40
Trying to design a PFC bank for medium voltage application, 10kV system voltage and measuring the system harmonics, I found out that the even number harmonics are really big: 4,65% the second order current harmonic, 2% the 4-th and 1.25% 6-th harmonic. Also pretty big was the third and triplen harmonics (third harmonic level 3.7%)As the desired sollution was to implement a passive filter with three branches for 5-th, 7-th and 11-th harmonics - which are the biggest), the existence of the 4-th and 6-th harmonics rises difficult problems regarding the amplification of these harmonics in the presence of the filter. Can anyone explain which is the possible cause of these un-characteristic harmonics ? The plant is packed with power SCR converters(6 and 12 pulses) and VFD drives, supplied on low voltage.
Thank you!
Pafi
Thank you!
Pafi