It is proposed to excavate below a community building to create basement areas. The building is about 30 years old and most of the foundation elements consist of grade beam on straight shaft bored cast in-place piles. There are also two existing basement locations under the building.One was created with the original construction and the other was done about 6 years after
The sizes of piles are 16 and 24 inch in diameter and the depth of embedment below ground varies from 22 to 27 feet. The shaft adhesion was backfigured to be 612 lbs/ft2. It is proposed (1) to excavate to grade beam and construct basement wall on footings or (2) to stay some distance away from piles say 4 ft and construct basement walls and footings. This would leave a strip of earth around piles.
Option 2 implies that despite the excavation and reduction of overburden stress caused by the excavation, not exposing the piles would allow them to maintain close to their original capacities. This concept suggests that despite the excavation there should be a distance away from the piles which an excavation can be done that does not influence the original capacity of the piles.
The design load of one of the 24 inch piles is 37 kips. The ground water is at 10 feet below ground and the soil is soft to firm silty clay with moisture contents from 35 to 42%. SPT in top 10 ft is 4. Pocket pen below 10 ft varies from 1 to 1.5 tons/ft2, maximum would be 2.
Questions:
1. How would you approach the determination of the capacity of existing piles before and after excavation re total or effective stress evaluation, Assume that end bearing is negligble and shaft adhesion governs. What capacity would you provide before and after.
2. Do you believe that leaving the strip of soil next to the piles, assuming the strip can stand, maintain the original allowable capacity (FOS 2) which is assumed as 37 kips for the pile in question.
3. Would you be comfortable excavating under this building or would you suggest underpinning.
4. If you believe in 2 re leaving strip of soil, how wide should that strip be and reasons.
Previous geotechnical report is unavailable. Recent geo information suggests the shaft resistance of 612lbs/ft2(unfactored/ultimate/without FOS etc) is reasonable. It is assumed that the piles reached their prescribed length.
The sizes of piles are 16 and 24 inch in diameter and the depth of embedment below ground varies from 22 to 27 feet. The shaft adhesion was backfigured to be 612 lbs/ft2. It is proposed (1) to excavate to grade beam and construct basement wall on footings or (2) to stay some distance away from piles say 4 ft and construct basement walls and footings. This would leave a strip of earth around piles.
Option 2 implies that despite the excavation and reduction of overburden stress caused by the excavation, not exposing the piles would allow them to maintain close to their original capacities. This concept suggests that despite the excavation there should be a distance away from the piles which an excavation can be done that does not influence the original capacity of the piles.
The design load of one of the 24 inch piles is 37 kips. The ground water is at 10 feet below ground and the soil is soft to firm silty clay with moisture contents from 35 to 42%. SPT in top 10 ft is 4. Pocket pen below 10 ft varies from 1 to 1.5 tons/ft2, maximum would be 2.
Questions:
1. How would you approach the determination of the capacity of existing piles before and after excavation re total or effective stress evaluation, Assume that end bearing is negligble and shaft adhesion governs. What capacity would you provide before and after.
2. Do you believe that leaving the strip of soil next to the piles, assuming the strip can stand, maintain the original allowable capacity (FOS 2) which is assumed as 37 kips for the pile in question.
3. Would you be comfortable excavating under this building or would you suggest underpinning.
4. If you believe in 2 re leaving strip of soil, how wide should that strip be and reasons.
Previous geotechnical report is unavailable. Recent geo information suggests the shaft resistance of 612lbs/ft2(unfactored/ultimate/without FOS etc) is reasonable. It is assumed that the piles reached their prescribed length.