Brimy
Electrical
- Apr 16, 2002
- 13
We are experiencing instantaneous magnetic breaker trips (1100 Amp setting) when transfering between normal and backup hydraulic systems. The system consists of two 60hp, 460V, 71FLA, Induction motors (Design type B). Each motor runs it's own hydraulic pump to a common hyd system. Each motor has it's own feeder breaker and reduced voltage starting autotransformer (set at 65%). When starting a motor with no hydraulic pressure, I measure a normal peak current of 240 amps, but the trips have occured when transfering from a running motor to backup motor when the meter peaks at it's maximum 600A rating. Considering inrush current and LRA I don't see how we are getting close to the 1100 Amp trip. I'm considering raising the tap to 80% for higher starting torque, any other ideas?