Excitation current on induction motor as a generator via VFD 2

jraef

Electrical
May 29, 2002
11,360
Hey fellow drive gurus, I have one that I have never come across before. I have a client wanting to use an 40HP (30kW) 460V induction motor on a water turbine pump and have the water overhaul it to turn it into an induction generator. So far so good, I’ve done that before. But the new twist is that they want to do this with a VFD, so that they can continue to get power out of it when water flow is lower than normal, also not a problem as I have done regenerative drives many times. The kicker for me this time is that they want this to NOT be connected to the grid, which means no excitation power, which means it cannot be self starting. They will feed the DC bus of the drive to another inverter to make AC power for a building nearby.

Their solution is to use a small cheap 120V portable generator to feed excitation power at start-up, and they seem to think they can do this with a small 3kVA step up single phase transformer that will connect 480VAC to two of the VFD line terminals, essentially a single phase input (which is possible with the drives they are using), then let that provide initial excitation energy to the motor windings (through the inverter of course) and once the motor is spun up and overhauled, it will provide its own excitation via the DC bus to be self sustaining.

The problem I am having is the AMOUNT of excitation current they will need to pull this off, and can a 3kVA single phase transformer supply that? As a general rule when I have done induction generators and have had to estimate excitation current (flux current) I have used 20% of the motor current as a safe bet. So using that, the motor is rated 50A, 20% would be 10A, which if coming from a single phase source, becomes 17A and the max amps out if a 3kVA 480V step-up transformer is just over 6A. I’m thinking this can’t work.

But I’ve never had to worry about this with a VFD before, because they have always been connected to a line source to where that is not an issue. In this case they say they had one that was doing it this way in the past, but the drives died years ago and never put put back in service, now there is nobody left who understood the original system. We just have drawings showing this 3kVA source input. So I can ASSUME it worked, but I’m unclear on the physics of excitation current in a VFD situation. Have I been over estimating the excitation current value at 20% for all these years because it didn’t really matter until now? I know that excitation current may be high because the PF is extremely low at startup, but maybe the VFD output might be using the DC bus caps to keep the RELATIVE line current much much lower?
 
Replies continue below

Recommended for you

Several references give the PF of an induction motor under full load as 90%.
1 2 = 1
0.9 2 = 0.81
1 - 0.81 = 0.19
Root 0.19 = 0.436, or 43%
20% may be a little low.
That said, if 20% has worked in the past, you may not need full excitation to start induction generation.
 
Last edited:
Have you considered self-excitation with a 3-phase capacitor-bank instead of external power supply? The logic is that residual magnetism from the rotor causes small induced voltage, which then causes larger current because of the resonance in the capacitors, and the machine self starts. Here's one article regarding wind turbine application (which I guess is not that far away from a water turbine)


As far as I know, magnetizing current can be much higher than 20% (I have seen values typically 40...50% as you also pointed out). But like you said, you don't need very high flux at no-load because there is no torque, so probably it works with the assumption of 20%
 
My guess is that exiting the generator with quite small external power via an VFD will work quite well. You just have to provide the losses during the startup process. But the issue is feeding into the grid. Usual active frontends are not designed to work without a grid. You need a grid forming inverter for this, e.f. like in an UPS.

Connecting capacitors parallel to the motor will not work if you use a VFD. The VFD will report a fault or blow up.
 
Jeff

415 V, 25 KW, 50 A, 1500 RPM motor no load testing with VFD in our shop today

VFD input - 396 V, 6.66 A, 2.7 KW, 0.998 PF
VFD output - 415.8 V, 19.6 A, 1.2 KW

Hope it helps.
 
At this point they are not connecting to the grid, and I have warned them that using VFDs will not allow that because no VFDs I know of have UL-1741 listing, which is necessary to get a NEM contract with a utility.

Thanks everyone for the info and help.
 
A question and a suggestion Jeff.
Can they use the water to spin up the turbine or is there an issue with flow control?
Suggestion; I am wondering if even a small excitation will boot-strap the motor and cause it to start self exciting?
Will the VFD pick up the motor on the fly?
 
Since an induction generator only generates power, but not voltage, where's the voltage going to come from? Even with caps to supply vars, there needs to be a solid voltage source to get any meaningful amount of power out of the generator. Don't think that's something the VFD can do. But I guess we'll have to wait and see...
 
I once set up a demonstration for some students in a vocational school shop.
A three phase induction motor coupled to a DC motor.
I connected a resistor bank in parallel with the AC motor.
I started the AC motor on the normal supply.
Then I ran up the DC motor until it was over-speeding the AC motor.
Then I cut the AC to the AC motor.
It continued to supply current to the resistor bank, with no electrical power in, just mechanical power from the DC motor.
I don't remember the meter readings.
The current may have been more than could be attributed to residual magnetism.
It was over 40 years ago.

where's the voltage going to come from?
Back EMF?
 