Hey,
Currently working on a police project with an evidence storage room. I am looking for some kind of guidance on recommended exhaust rates for this type of space. 62.1 does not specifically address this kind of room, although I had though about using the same rate for a chemical storage room (1.5 CFM/SF). I found a newsletter online from the Illinois Association of Property and Evidence Managers that mentions ASHRACE (how they spelled it...) recommends at least 10-12 ACH, but they do not cite the source nor could I find anything in the handbooks mentioning this. The owner specifically requested that the space be heavily exhausted due to smell from narcotics, I am just trying to gauge what a reasonable value is without going overboard.
Thanks in advance,
Jon
Currently working on a police project with an evidence storage room. I am looking for some kind of guidance on recommended exhaust rates for this type of space. 62.1 does not specifically address this kind of room, although I had though about using the same rate for a chemical storage room (1.5 CFM/SF). I found a newsletter online from the Illinois Association of Property and Evidence Managers that mentions ASHRACE (how they spelled it...) recommends at least 10-12 ACH, but they do not cite the source nor could I find anything in the handbooks mentioning this. The owner specifically requested that the space be heavily exhausted due to smell from narcotics, I am just trying to gauge what a reasonable value is without going overboard.