nuuvox000
Mechanical
- Sep 17, 2019
- 344
I'm trying to figure out how much exhaust CFM I would need to provide to cool an electrical room with transfer air from surrounding spaces. It has a 115 kVA transformer inside; it looks like these are typically about 95% efficient so 5% would be given off as heat in the room. So I'm looking at about 5.75 kW, which is about 19,600 BTU/hr. I'd like it to turn on at 90 °F and turn off at 85 °F. Air would be coming from the corridors at approximately 75 °F.
My equation for sensible gain is CFM*1.1*▲T*AF
CFM = cubic feet per minute
1.1 = constant in BTUh/CFM-°F
▲T = temperature difference
AF = altitude factor (0.85836 at my altitude)
So CFM = q_s/(AF*1.1*▲T)
19600/(0.85836*1.1*(90-75)) = 1385 CFM
Am I right in using this equation? Thanks in advance.
My equation for sensible gain is CFM*1.1*▲T*AF
CFM = cubic feet per minute
1.1 = constant in BTUh/CFM-°F
▲T = temperature difference
AF = altitude factor (0.85836 at my altitude)
So CFM = q_s/(AF*1.1*▲T)
19600/(0.85836*1.1*(90-75)) = 1385 CFM
Am I right in using this equation? Thanks in advance.