Exhausting heat from electrical room - check my calcs?

Status
Not open for further replies.

nuuvox000

Mechanical
Sep 17, 2019
344
I'm trying to figure out how much exhaust CFM I would need to provide to cool an electrical room with transfer air from surrounding spaces. It has a 115 kVA transformer inside; it looks like these are typically about 95% efficient so 5% would be given off as heat in the room. So I'm looking at about 5.75 kW, which is about 19,600 BTU/hr. I'd like it to turn on at 90 °F and turn off at 85 °F. Air would be coming from the corridors at approximately 75 °F.

My equation for sensible gain is CFM*1.1*▲T*AF

CFM = cubic feet per minute
1.1 = constant in BTUh/CFM-°F
▲T = temperature difference
AF = altitude factor (0.85836 at my altitude)

So CFM = q_s/(AF*1.1*▲T)
19600/(0.85836*1.1*(90-75)) = 1385 CFM

Am I right in using this equation? Thanks in advance.
 
Replies continue below

Recommended for you

You wouldn't get down to 85F though.

I calculated about 1800 CFM.

That's a lot of air....

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Thanks for the response, I'd love to know how you calculated that if you have time. Yes, and there are three of these rooms so it's 3 times a lot of air. My plan is to recommend mini splits for these spaces but I just wanted to make sure I had calcs to back it up too.
 
The equation you are using is correct. I don't know about the altitude correction factor but the basic equation is correct.

I have a spreadsheet attached from the previous company I worked for that estimates heat loads from electrical equipment. Attached is spreadsheet for transformers. For 112.5 kVA transformer heat load is 11,604.2 btu/hr.

Based on this and the equation assuming the correct altitude correction factor I calculate the air flow required = 820 CFM for 90 F resulting temperature.

The actual maximum design temperature for electrical equipment is 104 F, based on this the actual air flow required = 420 CFM approx.
 
Thanks, Snickster! I think you're right that I could take up the temperature in the room. It's still a lot of air and we're going to be doing a heat recovery VRF system anyway, so I'm going to push them to fan coils unless they really push back and want exhaust.
 