Here's the situation: the contractor was commissioned by the schoolboard direct to re&re windows on the ground floor. At present windows have been fabricated and they have started to install them. When they began to remove the existing windows they found that there was glass block above (hidden due to finishes), and that it was bearing directly on the window assemblies! There's no lintel or anything other than the frame to bring the load to grade. Severe deflection was noted in the block after they removed the first window.
Biggest thing is the original goal was to get students back into class by Jan 4th. Well, they have to for sure, but the goal was to have the work done by then so we're on a clock and hopefully can find something quick to do!
The windows vary in size but are 14-18ft long and appear to span between a CMU wall and a mid W-column. We are still waiting on approval to perform destructive openings so I can see all the existing framing / confirm member sizes. But I want to get ideas flowing so while things are open I have a good idea of what I might want to do (everything closed back up to get kids back to class come Jan 4th).
I'm a bit troubled given the size of the opening since it falls well outside the prescriptive tables in the code and if I run deflection calcs on a simply supported angle across the entire opening it is just a non-starter based on the info i've been provided in terms of amount of block, other loads, etc (I also am limited to maybe 3/8" angle or less since windows are already fabricated that close to the block). That said, I can potentially put vertical members in-between the windows since they come in individual pieces at 3-4ft length or so. I'd have them cover up the gap with sprayfoam / white flashing. My concern then would be out of plane suction wind loads. I'd need something more than just friction to rely on so I'd have to secure the angle to the block with some sort of anchor/stud/whatever. Does anyone have a good detail for glass block like that? I cannot recall a glass block job where I've ever had to tie into one and dont really know if there is anything strange with drilling into them (gut says there has to be)?
Note that the new steel lintel option will invariably involve shoring / needle beams / whatever and that'll take us into pretty extensive exterior repairs that were not planned for and the like. So while conventional and I suppose seemingly the simplest it wont be fast / cheap.
I also had the passing thought of carbon fiber wrapping the bottom blocks on inside/outside/underneath to effective make a beam that'll work for all directions. I'm not sure if carbon fiber wrap is suitable for a glass block substrate though and will need to put a call into the manufacturer. This idea mainly comes about because it would be cool to try lol if I am being honest
I'm not sure any of my ideas will work to get the students back into place by the deadline though, which is the biggest thing. If anyone has any wonderful ideas that can be done pronto / quick so the deadline can be met that would be awesome! If not, if you have better ideas but that take longer I'll take those as well
Biggest thing is the original goal was to get students back into class by Jan 4th. Well, they have to for sure, but the goal was to have the work done by then so we're on a clock and hopefully can find something quick to do!
The windows vary in size but are 14-18ft long and appear to span between a CMU wall and a mid W-column. We are still waiting on approval to perform destructive openings so I can see all the existing framing / confirm member sizes. But I want to get ideas flowing so while things are open I have a good idea of what I might want to do (everything closed back up to get kids back to class come Jan 4th).
I'm a bit troubled given the size of the opening since it falls well outside the prescriptive tables in the code and if I run deflection calcs on a simply supported angle across the entire opening it is just a non-starter based on the info i've been provided in terms of amount of block, other loads, etc (I also am limited to maybe 3/8" angle or less since windows are already fabricated that close to the block). That said, I can potentially put vertical members in-between the windows since they come in individual pieces at 3-4ft length or so. I'd have them cover up the gap with sprayfoam / white flashing. My concern then would be out of plane suction wind loads. I'd need something more than just friction to rely on so I'd have to secure the angle to the block with some sort of anchor/stud/whatever. Does anyone have a good detail for glass block like that? I cannot recall a glass block job where I've ever had to tie into one and dont really know if there is anything strange with drilling into them (gut says there has to be)?
Note that the new steel lintel option will invariably involve shoring / needle beams / whatever and that'll take us into pretty extensive exterior repairs that were not planned for and the like. So while conventional and I suppose seemingly the simplest it wont be fast / cheap.
I also had the passing thought of carbon fiber wrapping the bottom blocks on inside/outside/underneath to effective make a beam that'll work for all directions. I'm not sure if carbon fiber wrap is suitable for a glass block substrate though and will need to put a call into the manufacturer. This idea mainly comes about because it would be cool to try lol if I am being honest
I'm not sure any of my ideas will work to get the students back into place by the deadline though, which is the biggest thing. If anyone has any wonderful ideas that can be done pronto / quick so the deadline can be met that would be awesome! If not, if you have better ideas but that take longer I'll take those as well