phuduhudu
Structural
- Apr 19, 2001
- 261
There is an existing roof slab which had 105mm brick partition walls under. These have been removed but now the slab spans from the edges 7m x 9m. I was asked to look at it. Including screeds the slab is 210 thick. We took out some small areas of honeycombed concrete and found undeformed 12mm bars running in both directions at approx 200mm centres. I am having someone drill through the slab so we can get the exact thickness and checking the bar spacing with a cover meter. when I do the calcs (making many assumptions0 it doesn't work as it is. I have had it propped meantime but we will need a permanent solution. The client could accomodate one central column. Any ideas on how to go about this. Carl Bauer