hoangvhuy

Structural
Jun 4, 2016
18
Hi everyone,
i am designing structure for a hotel, 12 stories, 200m long. all is reinforce concrete
For normally, we need seperate 3 block by expansion joints, but it makes many difficult problem because architectural design is complicated, non-regular, if building have expansion joint, the joint will seperate the basement,lift core, swimming pool. And impact to facade of hotel.
So, Anybody have experience about same long project, what is best solution?
Can I use post poured strip to deal with that.
Thank for your sharings.
Screenshot_2022-12-23_163200_dvvlru.png

Above is layout of project
 
Replies continue below

Recommended for you

You may have to get a little creative... like

Clipboard01_krwaw6.jpg


and you may have a different pattern on each floor, but the joints should be placed, in particular if it's a high class building. Your architect should provide you with locations of joints in his finished exterior wall system; if he doesn't have them, there could be problems. Joints typically show up on building elevations and are normally required. The joints don't have to be large... 3/4" (20mm) or so...

another website that may be able to help:




-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
Another thought... I hope you are not in a high seismic area. We're not, and I missed that because seismic loading and deformation is not undertaken here.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
hi @dik
Lucky, this project is in weak( low) - seismic area, don't need calculate seismic resistance
 
@hoangvhuy
Time to have a sit down with architect and developer as the joints will be required. Architect will have to shift things to accomodate these joints.
How is the ground, is it uniform along the length?
 
YuleMsee, sums it up, "as the joints will be required."

As noted earlier, "Your architect should provide you with locations of joints in his finished exterior wall system; if he doesn't have them, there could be problems." I'm not trying to be difficult, but with a building with that irregular 'footprint', if you don't have joints, you will likely have serious problems.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
hi YuleMsee,
Ground floor is not uniform along the length, and there are 03 level for ground, so, difficult to put in expansion joint.
mat_cat_mui_dinh_m834pd.png
 
The cross section poses some other issues. The differences in elevation or building type will require careful location of joints. The building types should be largely isolated. You are looking at some significant joints and the problem is not an easy one. KWhere joints are below grade, they will/should be waterproofed.

-----*****-----