Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

expansion valve adjustment

Status
Not open for further replies.

reftec021702

Mechanical
Mar 19, 2007
10
0
0
PA
Dear fellows:

I have two YORK 10-ton dual circuit evaporators not working at full capacity. Superheat measurements indicate values above 25 degrees F. I would like to reduce the superheat setting of the valves, but they seem to be of a fixed non-adjustable type. Is there any way to make them open a little bit, or need to change the all ? Thank you!!
 
Replies continue below

Recommended for you

As a refrigeration mechanic I watch this forum regularily to get a very valuble perspective on design and engineering.

Adjusting expansion valves is trade talk.

Go to
You'll find more than enough people on that site willing to impress thier 'wisdom' on anyone who asks.
 
You may have other issues such as
1.Do you have the proper line sizes
2Is the head pressure high enough to give you a full head of liquid at the TXV
3.Is the sub cooling between 10-15*F
4.Do you have a restriction in the liquid line (bad drier) etc
5.Do you have the correct CFM air flow
6.TheSuperheat should be in the range of 12 to 20?F, no more than 25?F 6" from compressor suction valve. Superheat in the normal range indicates the valve is probably working properly, but further investigation should be made.

 
Status
Not open for further replies.
Back
Top