csgasbm
Petroleum
- Apr 3, 2006
- 7
I recently had the pleasure of being 2ft away from an enclosure which housed a 40HP VFD when an internal capacitor blew. The events leading up this are as follows:
Power supply: 100kVa 480V Generator
VFD: 40HP Yaskawa G5 (Current rating 51A)
Load: submersible pump consisting of a 20HP 3450rpm motor @ 1800ft down a well. FLA: 28A
1. Attempted to start the pump, only to have it trip on DC bus overvolts twice, then start on the third attempt (restarts where automatic and in quick succession)
2. Appart from the problems at startup, the pump seemed to operate OK (current and torque readings back to the drive were good) and we had pumped water to the surface for some time.
3. I then attempted to switch the controller from manual to auto speed (the VFD changes speed to maintain a set water level), which due to the water level I expected the pump to increase speed to the frequency upper limit (which was set to 90% of the full speed).
4. Instead the VFD tripped on Overcurrent (again, the drive attempted to autorestart but this time stayed down on the third attempt). It was then that a burning smell was noticed from the unit, followed very quickly by an explosion.
5. After a change of underwear and a lot of fingerpointing at the drive (by everyone but me), we installed an identical drive in it's place, only to have the same overvoltage trip occur on a manual speed startup.
6. I then convinced the techs to wire up a small 5HP motor we happened to have nearby to see if it will run it without any probs, which worked.
My questions are (never really having to much experience with hardware probs)
1. Is it safe to say the downhole motor is the problem? (it seems to run OK in manual speed; apart from the startup problems, and the electricians tell me that it meggars fine)
2. What actaully goes on in the drive to cause the bus capacitor to explode?
3. What other things could/should I be looking at to determine the prob?
Thanks for any help
Power supply: 100kVa 480V Generator
VFD: 40HP Yaskawa G5 (Current rating 51A)
Load: submersible pump consisting of a 20HP 3450rpm motor @ 1800ft down a well. FLA: 28A
1. Attempted to start the pump, only to have it trip on DC bus overvolts twice, then start on the third attempt (restarts where automatic and in quick succession)
2. Appart from the problems at startup, the pump seemed to operate OK (current and torque readings back to the drive were good) and we had pumped water to the surface for some time.
3. I then attempted to switch the controller from manual to auto speed (the VFD changes speed to maintain a set water level), which due to the water level I expected the pump to increase speed to the frequency upper limit (which was set to 90% of the full speed).
4. Instead the VFD tripped on Overcurrent (again, the drive attempted to autorestart but this time stayed down on the third attempt). It was then that a burning smell was noticed from the unit, followed very quickly by an explosion.
5. After a change of underwear and a lot of fingerpointing at the drive (by everyone but me), we installed an identical drive in it's place, only to have the same overvoltage trip occur on a manual speed startup.
6. I then convinced the techs to wire up a small 5HP motor we happened to have nearby to see if it will run it without any probs, which worked.
My questions are (never really having to much experience with hardware probs)
1. Is it safe to say the downhole motor is the problem? (it seems to run OK in manual speed; apart from the startup problems, and the electricians tell me that it meggars fine)
2. What actaully goes on in the drive to cause the bus capacitor to explode?
3. What other things could/should I be looking at to determine the prob?
Thanks for any help