I designed both recovery boilers and fluidized beds. I know the exact answer to your question. For the people curious about what explosion corner is I can explain that it is to make one or more of the furnace wall corner connections much weaker than the others so that in the case of explosion happens inside, the corner seal will quickly break and let the pressure out. This is much more effective than the traditional explosion doors which open slowly and typically do not have enough opening areas for releasing the explosion gas.
The explosion corner design came from recovery boilers and the explosion corner guideline is from BLRBAC (Black Liquor Recovery Boiler Advisory Committee) particular to pulp and paper industry because explosion damage coming from water contacting with the blazing char bed can cause severe explosion damages and there is no other good way to deal with it rather than to open up the furnace walls. I have heard that explosion corners and other important safety designs according to BLRBAC guidelines have saved lifes in paper mills. The BLRBAC site is below:
Unfortunately I have not seen NFPA guidelines adopting the explosion corner design. I saw only NFPA asks to design the furnace and connecting ductwork to resist minimum +/-35 inches WG. This is more of for holding the pressure inside rather than releasing it. The common knowledge is that explosion pressures are always much higher than 35 inches so things can still break and damages can happen at unpredicable places. The idea of explosion corner is much better because it makes some thing weaker and you always know where is going to break and just need to be sure not to get close to it then you will be safe. I think this is exact the reason of you asking question but the reality is the other way. Due to lack of guidelines and the ineffectiveness of the traditional explosion door designs, many coal-fired boilers have even gotten rid of the explosion doors so there is almost no good protection against furnace explosion at this moment.
Even though there is no good guideline for CFB and BFB, for European designs they have already made the explosion corners standards to all the CFB/BFB products including those sold to US but there could be always debates among US clients regarding using it or not so some of the US customized designs were changed back to solid corners.
I don't know what's in NFPA's mind but what I can think of that the reasons of not using the weak corners are:
1. If you don't barricade or limit access to the areas around the outside of the weak/explosion corners, it is even more dangerous and becomes safety hazard. Recovery boiler users always know about it and even avoid putting platforms near the corners but this is not the case for the most PC plus CFB and BFB customers.
2. Weak/explosion corners tend to crack open prematurely if you have a lot of furnace pressure variations which cause the fatigue on the weak corner seal material. You start to see sparks coming out of the corners and this becomes maintenence nightmare to certain clients. If otherwise the furnace holds constant negative pressures then there is not such problem.
3. It is a little bit harder to install explosion corners and need special attentions. Bad installations can cause premature failures.
The above are not big problems and can be easily caken care of. Besides, having weak corners can also reduce the cost of materials because do not have to design things very strong now. One more advantage is that, if NFPA adopts it and customers use the design, I am sure the insurance companies will follow up and consider this to be a good safety feature for the boiler and will then lower the customer's payments.
Overall, as my opinion explosion corner is really a good and only working design for safety against explosion and it should be a must-have for all boilers and NFPA should adopt it. In addition, NFPA should also pay attention to what I mentioned above and add terms to avoid access to the surrounding areas and, that's it.