Explosion Proof RTD's

Status
Not open for further replies.

danw2

Industrial
Oct 21, 2004
1,505
I must have missed a previous thread, RTD's Intrinsically Safe,
Link
Just found it in a search.

(Keith) >Never seen an ExP RTD before. Seems likely to lag the poor thing horridly. I could see them wanting to change out ExP for two reasons. One would be having to run the requisite thick-wall conduit and bulkhead plugging hassles and the other would be maybe needing a more responsive sensor.
-----------------

There's no lagging on the sensing element. Because the RTD is a 'simple apparatus', it's the screw cover head that is Class 1, Div 1 rated, not the sensing element.

Pyro_Hazardous_Area_Heat_Trace_RTDs_emdl2c.jpg
 
Replies continue below

Recommended for you

Are you looking at a RTD or heat trace? In the past, I would spec a RTD in a thermowell. Then we would use C1, D2 wiring methods. If the "probe" had direct contact w/ a process, then I would go w/ IS.