Hope this helps.7.3 Vaults and Pads for Service Equipment - 7.3.1 Vaults
Suitable screening should be used to prevent birds, insects, vermin, or rodents from entering the shaft. The ceiling, walls, and floor should be of fire-resistant construction. Reinforced concrete is preferred. When oil insulated transformers are used and persons occupy the area adjacent to the vault wall, or when an explosion may otherwise damage a building wall, the vault walls should be sufficiently strong to withstand an explosion. The hazard may also be reduced by limiting the ratio of vault volume in cubic feet to net ventilated area in square feet. Tests indicate that where this ratio does not exceed 50:1, an 8 inch reinforced concrete wall will suffice.