Having some differences of opinion with a client and a supplier (...I can hear you grinning from here...)
IEC 60079-14 paragraph 6.4
In the design of electrical systems, steps shall be taken to reduce to a safe level the effects of static electricity.
I have 5% HCl acid line (PTFE lined stainless pipe, exterior 400 microns painted) in a zone 2 area. Zoned due to hydrogen producing electrolyers nearby.
Exterior marine environment.
PTFE liner isolates from conductive liquid. All equipment ICEEx rated.
Do I need bonding across pipe flanges, specifically to reduce risk of incendive discharge from static build up? The client is suggesting wind blowing over the 2" pipe spools will accumulate static charge on painted exterior surface.
I note, nothing has been mentioned of static present on operators discharging against earthed pipe and structure. Nor have we been asked to make entire surface of painted pipe conductive, just provide bonding. Nor has anything been mentioned about the whole steel structure being painted in same paint system, presumably also non-conductive and exposed to same wind. Nor has anything been mentioned about the huge non-conductive GRP tanks adjacent.
To be fair any hydrogen escaping from the elctrolysers about 3m away is going to go straight up and not hang about. I don't really know why the area is zone 2, but that is not my area and I am not challenging that at all.
I have been referred to IEC 60079-14 para 6.4 (which I have quoted above) which is not really helpful. And also IEC 60092-502 sub-section 5.5 which I don't yet have and am waiting for the office to receive.
Anyone else come up against this? I can't see how bonding the pipe across flanges gets rid of static in middle of pipe spool. Surely all the spool needs to be conductive? And if all pipe spools surfaces then all painted steelwork surfaces? i.e. the paint system should be conductive?
IEC 60079-14 paragraph 6.4
In the design of electrical systems, steps shall be taken to reduce to a safe level the effects of static electricity.
I have 5% HCl acid line (PTFE lined stainless pipe, exterior 400 microns painted) in a zone 2 area. Zoned due to hydrogen producing electrolyers nearby.
Exterior marine environment.
PTFE liner isolates from conductive liquid. All equipment ICEEx rated.
Do I need bonding across pipe flanges, specifically to reduce risk of incendive discharge from static build up? The client is suggesting wind blowing over the 2" pipe spools will accumulate static charge on painted exterior surface.
I note, nothing has been mentioned of static present on operators discharging against earthed pipe and structure. Nor have we been asked to make entire surface of painted pipe conductive, just provide bonding. Nor has anything been mentioned about the whole steel structure being painted in same paint system, presumably also non-conductive and exposed to same wind. Nor has anything been mentioned about the huge non-conductive GRP tanks adjacent.
To be fair any hydrogen escaping from the elctrolysers about 3m away is going to go straight up and not hang about. I don't really know why the area is zone 2, but that is not my area and I am not challenging that at all.
I have been referred to IEC 60079-14 para 6.4 (which I have quoted above) which is not really helpful. And also IEC 60092-502 sub-section 5.5 which I don't yet have and am waiting for the office to receive.
Anyone else come up against this? I can't see how bonding the pipe across flanges gets rid of static in middle of pipe spool. Surely all the spool needs to be conductive? And if all pipe spools surfaces then all painted steelwork surfaces? i.e. the paint system should be conductive?