Two questions- First, is anyone aware of research and/or a design method for an extended or flush end plate conn that is welded to the supporting column rather than bolted? The AISC design guides 4 and 16 address only field bolted end plates. I have not found anything further on the web for a field welded end plate. The connection I want to design is not in a frame, its for a renovation, helping hold up several cantilever beams that carry a canopy attached to the exterior of existing building columns. The end plate connection will carry dead load, snow and wind. Field bolting may be very difficult due to existing conditions.
I would like to use fillet welds to attach the end plate to its supports. Before erection the cantilever could be shop welded to the end pl with cjp welds as needed. Doing some quick and approximate calcs using elastic theory and assuming the end pl is perfectly rigid, code minimum forces on the proposed welds seem small enough to do this, if I use an extended plate, but I would like to hear how someone else might have approached this condition.
This leads to my second question. Would it be best to develop the full bending strength of the cantilever with this end connection or should I use the code design forces, which are far less (deflection governs the cantilever beam size). I also am not sure if the supporting existing columns should be checked for just the code loads or instead for the forces resulting from developing the full bending capacity of the cantilever. Any feedback appreciated.
I would like to use fillet welds to attach the end plate to its supports. Before erection the cantilever could be shop welded to the end pl with cjp welds as needed. Doing some quick and approximate calcs using elastic theory and assuming the end pl is perfectly rigid, code minimum forces on the proposed welds seem small enough to do this, if I use an extended plate, but I would like to hear how someone else might have approached this condition.
This leads to my second question. Would it be best to develop the full bending strength of the cantilever with this end connection or should I use the code design forces, which are far less (deflection governs the cantilever beam size). I also am not sure if the supporting existing columns should be checked for just the code loads or instead for the forces resulting from developing the full bending capacity of the cantilever. Any feedback appreciated.