Background:
A steel, Aboveground Storage Tank (AST) built to UL142 standards and containing diesel fuel (Class II fuel). This is an atmospheric (low pressure) tank with operating pressures <= 1.0 psig but which may experience pressures as high as 2.5 psig when exposed to a fire (emergency conditions).
The tanks are equipped with an atmospheric (Normal) vent opening that are sized to keep pressures less than 1.0 psig when product is transferred into and out of the tank. They are also equipped with an Emergency Vent opening sized to keep the pressure inside the tank less than 2.5 psig when exposed to a fire with a specified heat input and a specified calculated discharge expressed in SCFH.
The Emergency Vent openings are sized assuming a 12” long nipple extending from this vent opening. When this Emergency Vent piping needs to be extended, to terminate outside a building for example, the additional length of piping and pipe fittings (elbows, etc.), a significant reduction in vent flow can occur unless the size of the vent and connecting piping is increased. In such cases, the size of vent and vent pipe extensions need to be calculated to ensure that that tank will not experience pressures greater than 2.5 psig.
Given:
A 400 gallon UL142 AST containing diesel fuel with a 4” diameter emergency vent opening and a required emergency venting capacity of 94,800 SCFH. The Emergency Vent piping needs to be extended 28’ from the tank and will have three long radius (r/d=1.5) pipe bends. The piping will terminate outside into the atmosphere and will include an Emergency Vent cap at the termination point that is designed to remain closed until it reaches 0.5 psig when it opens and releases the vapor in the piping.
Problem:
What is the pressure inside the tank with the extended Emergency Vent piping and fittings? Or put another way, what discharge can flow through this extended piping and fittings to keep the pressure inside the tank less than 2.5 psig?
This is my first posting so hope the format is OK. Thanks for any help.
A steel, Aboveground Storage Tank (AST) built to UL142 standards and containing diesel fuel (Class II fuel). This is an atmospheric (low pressure) tank with operating pressures <= 1.0 psig but which may experience pressures as high as 2.5 psig when exposed to a fire (emergency conditions).
The tanks are equipped with an atmospheric (Normal) vent opening that are sized to keep pressures less than 1.0 psig when product is transferred into and out of the tank. They are also equipped with an Emergency Vent opening sized to keep the pressure inside the tank less than 2.5 psig when exposed to a fire with a specified heat input and a specified calculated discharge expressed in SCFH.
The Emergency Vent openings are sized assuming a 12” long nipple extending from this vent opening. When this Emergency Vent piping needs to be extended, to terminate outside a building for example, the additional length of piping and pipe fittings (elbows, etc.), a significant reduction in vent flow can occur unless the size of the vent and connecting piping is increased. In such cases, the size of vent and vent pipe extensions need to be calculated to ensure that that tank will not experience pressures greater than 2.5 psig.
Given:
A 400 gallon UL142 AST containing diesel fuel with a 4” diameter emergency vent opening and a required emergency venting capacity of 94,800 SCFH. The Emergency Vent piping needs to be extended 28’ from the tank and will have three long radius (r/d=1.5) pipe bends. The piping will terminate outside into the atmosphere and will include an Emergency Vent cap at the termination point that is designed to remain closed until it reaches 0.5 psig when it opens and releases the vapor in the piping.
Problem:
What is the pressure inside the tank with the extended Emergency Vent piping and fittings? Or put another way, what discharge can flow through this extended piping and fittings to keep the pressure inside the tank less than 2.5 psig?
This is my first posting so hope the format is OK. Thanks for any help.